The following tables list the system specifications for VSP F350.
CBSS controller chassis
Item |
Specification |
---|---|
Physical dimension (W x D x H) (mm) |
483 × 813 × 88 mm |
Weight/Mass |
16.1 kg |
Start-up time (min)1 |
5 to 8 (min) |
Required height (EIA unit)2 |
2U |
Heat output (W) |
218 W |
Power consumption (VA) |
226 VA |
Air flow (m3/min)3 |
4.0 (m3/min) |
Notes:
|
DBS/DBSE drive chassis
Item |
Specification |
---|---|
Physical dimension (W x D x H) (mm) |
482 × 565 × 88.2 mm |
Weight/Mass (kg) (Approximate) |
17 kg |
Start-up time (min)1 |
5 to 8 (min) |
Required height (EIA unit)2 |
2U |
Heat output (W) |
116 W |
Power consumption (VA) |
126 VA |
Air flow (m3/min)3 |
2.2 (m3/min) |
Notes:
|
Drive type
Item |
Specification |
|
---|---|---|
Supported data capacity |
472.61, 945.23, 1890.46, 3780.92, 7561.85, 15048.49, 30095.00 GB |
|
Maximum storage system capacity (physical capacity) |
2,627 TiB (using 15 TB 2.5-inch SFF SSD) |
|
5,255 TiB (using 30 TB SSD) | ||
Maximum mountable quantity (unit)1 |
24 (total per chassis) |
192 (maximum per system) |
Maximum number of spare drives2 |
16 |
|
Note:
|
Host interface
Item |
Specification |
---|---|
Interface type |
16/32 Gbps FC (Optical) 10 Gbps iSCSI (Optical) 10 Gbps iSCSI (Copper) |
Data transfer speed (Max. speed for transfer to host) |
400 Mbps (FC) 800 Mbps (FC) 1600 Mbps (FC) 3200 Mbps (FC) 1000 Mbps (iSCSI - Optical) 1000 Mbps (iSCSI - Copper) |
Number of ports |
16/32 Gbps FC (Optical): 16 10 Gbps iSCSI (Optical): 8 10 Gbps iSCSI (Copper): 8 |
Transferred block size (bytes) |
512 |
Maximum number of hosts via FC switch |
255 |
Maximum number of hosts via network switch |
255 |
Battery life
Storage system intake temperature | CBSS |
---|---|
Up to 75.2º F (24º C) |
5 years |
Up to 86º F (30º C) |
5 years |
Up to 93.2º (34º C) |
4 years |
Up to 104º (40º C) |
3 years |
RAID specifications
Item |
Specification |
---|---|
RAID level* |
Flash drive mounted: 1/5/6 |
RAID configuration |
RAID1: 2D+2D, 4D+4D RAID5: 3D+1P, 4D+1P, 6D+1P, 7D+1P RAID6: 6D+2P, 12D+2P, 14D+2P |
Maximum number of parity groups |
64 |
Maximum volume size |
3 TB (when using the LDEVs of other Storage Systems: 4TB) |
Maximum volumes/host groups and iSCSI targets |
2048 |
Maximum volumes/parity groups |
2048 |
*A storage system configured with RAID6, RAID 5, or RAID 1 provides redundancy and enhances data reliability. However, there is still a possibility of losing data caused by unforeseeable hardware or software failure. Users should always follow recommended best practices and back up all data. |
Internal logic specifications (CBSS)
Item |
Specification |
---|---|
Control memory |
Flash memory: 32 MB L3 cache memory: 4 MB SDRAM: 1 GB |
Data assurance method |
Data bus: Parity Cache memory: ECC (1 bit correction, 2 bit detection) Drive: Data assurance code |
Cache specifications
Item |
Specification |
---|---|
Capacity (GB per system) |
128 GB |
Control method |
Read LRU/Write after |
Battery backup |
Provided |
Backup duration* |
Unrestricted (Saving to a nonvolatile memory) |
*Non-volatile data in the cache memory is protected against sudden power failure. The backup operation writes data into a cache, even if a power interruption occurs, and transferred to the cache flash memory. |
Insulation performance
Item |
Specification |
---|---|
Insulation withstand voltage |
AC 1,500 V (100mA, 1min) |
Insulation resistance |
DC 500 V, 10 MΩ or more |