The following figure and table describe the specifications of the PDU.
Figure. APAC and EMEA PDU for the
Hitachi Universal V2B Rack (Three-phase 3P16A-15C13-3C19CE.P)
Part number |
Region |
Quantity |
Power input per PDU |
Power output per PDU |
Total rack amperage available |
---|---|---|---|---|---|
3P16A-15C13-3C19CE.P |
APAC and EMEA |
4/rack 2/side |
Three phase 400V max. 16A (12.8A rated) 50Hz / 60Hz Delta/wYe: wYe IEC309 3P + N + E input power plug 4.5 m (14.76 feet) cable |
15 IEC C13 + 3 IEC C19 sockets Max allowable current: 38.4A 8.8kVA |
77A (17.6kVA) |