The following table provides some key technical specifications for VSP G130.
Item |
Specification |
|||
---|---|---|---|---|
System |
Number of disk drives (HDD) |
Minimum |
4 (disk-in model)/0 (diskless model) |
|
Maximum |
96 |
|||
RAID level |
RAID 6/RAID 5/RAID 1 |
|||
RAID group configuration |
RAID 6 |
6D+2P, 14D+2P |
||
RAID 5 |
3D+1P, 7D+1P |
|||
RAID 1 |
2D+2D, 4D+4D |
|||
Maximum number of spare drives |
161 |
|||
Maximum number of volumes |
2,048 |
|||
Maximum storage system capacity (physical capacity) |
201 TiB (using 2.4 TB, SFF HDD) 1,196 TiB (using 14 TB, LFF HDD) |
|||
Memory |
Cache memory capacity |
32 GiB |
||
Cache flash memory capacity |
BM05 |
|||
Storage interface |
Controller/drive chassis interface |
SAS/Dual Port |
||
Data transfer rate |
Maximum 12 Gb/s |
|||
Maximum number of drives per SAS interface |
144 |
|||
Channel interface |
Support channel type |
Open systems |
Fibre Channel Shortwave |
|
Data transfer rate |
||||
Fibre Channel |
400/800/1600 MB/s |
|||
Maximum number of channel adapters |
4 |
|||
Power |
AC Input |
Single-phase |
50Hz/60Hz : 100V to 120V, 200V to 240V |
|
Acoustic Level 2, 3 |
Operating |
CBSS/CBSL |
60dB (32°C) |
|
DBSC/DBLC |
60dB (32°C)4, 5 |
|||
Standby |
CBSS/CBSL |
55dB |
||
DBSC/DBLC |
55dB4, 5 |
|||
Non-stop maintenance |
Control PCB |
Supported |
||
Cache memory module |
Supported |
|||
Cache flash memory |
Supported |
|||
Power supply, fan |
Supported |
|||
Microcode |
Supported |
|||
Drive (2.5-inch/3.5-inch HDD) |
Supported |
|||
Notes:
|
Electrical specifications
The following table describes the electrical specifications for the VSP G130.
Input power specifications | CBSS/CBSL controller chassis | DBS/DBL drive tray |
---|---|---|
Input voltage (Operable voltage range) (V) |
AC 100-120/200-240 +6%/-11% |
AC 100-120 / 200-240 +6%/-11% |
Frequency (Hz) | 50/60 ± 1 | |
Number of phases, cabling | Single-phase with protective grounding | |
Steady-state current 100V/200V (A)1, 2 |
4.0×2/2.0×2 |
DBS: 2.4×2/1.2×2 DBL: 1.9×2/1.0×2 |
Current rating of breaker/fuse (A) | 16.0 (each electrical) | 16.0 (each electrical) |
Heat value (normal) (kJ/h) |
1770 or less |
DBS: 1120 or less DBL: 940 or less |
Steady-state power (VA/W)3 |
800/760 or less |
DBS: 480/460 or less DBL: 380/350 or less |
Power consumption (VA/W) |
490/490 or less |
DBS: 320/310 or less DBL: 280/260 or less |
Note:
|
Environmental specifications
Item | CBSS/CBSL controller chassis | DBS/DBL drive tray | Notes | |
---|---|---|---|---|
Temperature | Operating (°C) | 10 to 40 | 10 to 40 | - |
Non-operating (°C) | -10 to 50 | -10 to 50 | ||
Transport/storage (°C) | -30 to 60 | -30 to 60 | ||
Temperature change rate (°C) | 10 or less | 10 or less | ||
Humidity | Operating (°C) | 8 to 80 | 8 to 80 | - |
Non-operating (°C) | 8 to 90 | 8 to 90 | ||
Transport/storage (°C) | 5 to 95 | 5 to 95 | ||
Max. wet bulb temperature (°C) | 29 (non-condensing) | 29 (non-condensing) | ||
Vibration | Operating (m/s2) | 2.5 or less (5 to 300Hz) | 2.5 or less (5 to 300Hz) | Within 5 seconds (Resonance point: 10Hz or less) |
Non-operating (m/s2) |
5.0 or less (5 to 300Hz): No critical damage for product. 9.8 (1.0G): Ensure own safety with fall prevention. |
5.0 or less (5 to 300Hz): No critical damage for product. 9.8 (1.0G): Ensure own safety with fall prevention. |
||
Transport (packed) (m/s2) |
5.0 or less | 5.0 or less | - | |
Impact | Operating (m/s2) | 20 or less | 20 or less |
10ms, half sine wave |
Non-operating (m/s2) | 50 or less | 50 or less | ||
Transport (packed) (m/s2) |
80 or less | 80 or less | ||
Storage system tips over at specific angle (°) | 15° or less | 15° or less | To be measured when installed on leveling bolts. | |
Altitude | Operating (m) |
(5) to 3,050 (Environmental temperature: 10°C to 28°C) to 950 (Environmental temperature: 10°C to 40°C) |
- | |
Non-operating (m) | -60 to 12,000 | -60 to 12,000 | ||
Gaseous contaminants4 | Operating | G1 classification levels | G1 classification levels | - |
Non-operating | G1 classification levels | G1 classification levels | ||
Transport/storage | - | - | ||
Acoustic noise LpAm6, 7 (dB) | Operating | 60 (Environmental temperature: 32°C or less)1 | - | |
Standby | 55 | |||
Noise level (dB) | Operating (Recommended) | 90 or less3 | - | |
Notes:
|